A reading of 0 volts between Y and the coil input on line #11 under thermostat closed and fan auto indicates which condition?

Prepare for the ESCO Electrical Employment Ready Test. Utilize flashcards and multiple choice questions with hints and explanations. Achieve success on your exam!

Multiple Choice

A reading of 0 volts between Y and the coil input on line #11 under thermostat closed and fan auto indicates which condition?

Explanation:
When the cooling call is active, the thermostat must close the Y circuit and deliver 24 VAC from the R supply to the outdoor coil input. A reading of zero volts between Y and the coil input means no voltage is reaching the coil, so the coil won’t energize. That points to the thermostat not making the Y connection when it should, i.e., the thermostat is defective. If the thermostat were functioning, closing the cooling circuit would produce a voltage across Y and the coil input, energizing the outdoor coil. Other faults (like a short or a broken wire) would typically show different symptoms or readings, so the lack of voltage here most strongly indicates a defective thermostat.

When the cooling call is active, the thermostat must close the Y circuit and deliver 24 VAC from the R supply to the outdoor coil input. A reading of zero volts between Y and the coil input means no voltage is reaching the coil, so the coil won’t energize. That points to the thermostat not making the Y connection when it should, i.e., the thermostat is defective. If the thermostat were functioning, closing the cooling circuit would produce a voltage across Y and the coil input, energizing the outdoor coil. Other faults (like a short or a broken wire) would typically show different symptoms or readings, so the lack of voltage here most strongly indicates a defective thermostat.

Subscribe

Get the latest from Examzify

You can unsubscribe at any time. Read our privacy policy